Some
suggested reading in the "National Electrical Code"
: Article 250 on Grounding, article 280 Surge
Arrestors, article 285
Surge-Protective Devices.
Before
purchasing a surge suppressor you
should examine the main grounding
electrode and grounding electrode
conductor connected to your electrical
service. Lightning will usually follow
the most direct path of least
resistance to earth and you would
prefer that it does not detour through
any of your electronic equipment and
cause damage. Having an effective
grounding system will not only enhance
protection of your computer equipment,
but all electronic devices such as
TV’s, VCR’s, microwave ovens,
satellite dishes, and virtually
anything else that is electronically
or microprocessor controlled.
The
main grounding electrode for most
houses is the metal water pipe at the point
where it enters the home before the
water meter. Look at this area and you
should see a copper or aluminum wire;
bare, insulated, metal armor jacketed,
enclosed in conduit, or taped green.
It should be connected to the water
pipe using an approved ground clamp
usually of bronze construction. The
connection should be tight and free of
corrosion. If the ground clamp
and wire appear corroded or feel loose you should remedy this right
away. A new ground clamp costs only a
few dollars and can be purchased at
any electrical supply company and at
many home improvement stores. You will
also need some emery cloth or
sandpaper to clean the pipe. A good
precaution when doing this would be to
shut off the main circuit breaker or
pull the main fuse in your electrical
panel. It is possible that a tiny
amount of current may be traveling
over your grounding conductor. I also
suggest wearing gloves and avoid
touching the bare wire and the water
pipe at the same time.
If your
home gets it water supply from a
private well or through a plastic
pipe, your primary ground connection
will be a ground rod or two. In
many cases the ground rod(s) are
completely buried and therefore are
not easy to inspect. However if
your ground rod(s) are twenty five
years or more old then they should be
upgraded with new rods.
Something
to consider at this time is upgrading
your grounding system to the latest "National Electrical Code" requirements.
The current code requires that new
installations have at least one
supplementary ground rod installed and
to also have all interior metal piping
connected (Bonded) to the grounding
electrode system. In some
jurisdictions the requirement to bond
the interior gas pipes has been
waived. Check with your
local electrical inspector for the
correct procedure. A bonding jumper
wire is also required from one side of
the water meter to the other side to
maintain ground continuity on the
metal pipe if and when
the water meter is replaced. Read
article 250 in the latest edition of
the "National Electrical Code"
for all of the
requirements.
To
bring your house up to today’s
standards you will need the
following: Five, six or maybe more
ground clamps suitable in size and
compatibility with your water pipes,
gas pipe, heating pipes, and any other
interior metal piping, two
5/8" x 8’ copper clad ground
rods, two acorn style clamps
for ground rods, #6 or #4 copper wire
bare or insulated, 3/8" one hole
straps, an approved connector for the
grounding conductor,
green electrical tape if using
insulated wire, a ground bar for the
main electrical panel if there is no
available empty slot for a large wire,
an intersystem bonding termination and suitable staples for fastening the
ground electrode conductor wire.
Additionally
you will need the following tools
to
facilitate the installation of your
upgraded grounding system: Claw
hammer, 3 pound or heavier hammer to
drive ground rods, emery cloth or
sandpaper, flat head screwdrivers, and
heavy duty wire cutters or lineman
pliers, an adjustable wrench, and a six foot ladder. You may
also need a drill and drill bits
suitable for drilling through floor
joists, a hammer drill and masonry
drill bits to drill into masonry, and
a flat metal file. A rotary hammer
with a ground rod driver
attachment will make the
driving of the ground rods much easier
and quicker. An alternative is a
forty or sixty pound jack hammer in
which the ground rod can be inserted
directly into the bit holder.
The ease at which the ground rod goes
into the ground is determined by soil
conditions.
The
most difficult part of this job is
driving the ground rods. Although one
is the minimum standard set by the
"National Electrical Code",
two are often required due to soil
conditions. Soil resistance varies across town,
county, and state lines. Without
expensive detailed testing of your
soil, there is no way to determine if
it has a low or high resistance to
electrical current. Therefore to be on
the safe side it is better to drive
two ground rods. Eight foot ground
rods should be installed no less than
sixteen feet apart for optimum
performance and there is no
maximum distance restriction. Ten foot
rods should be at least twenty feet
apart.
Start
by choosing an area outside near your
electric meter that is free of
underground electric, water, gas,
telephone, oil, and any other utility
lines. Call 811 to arrange a markdown
of the area if you suspect underground
utilities are in place. Try to stay close to the house
but at least a foot away to avoid
contact with the concrete footings. Keep in mind
that you will need to run a wire from
the ground rods to your main electric
panel. You should plan on how you
intend to do that before proceeding
further. Generally speaking the
ground rods would be driven straight
down into the earth with the top being
slightly below the surface. A
continuous #6 or #4 wire would be run
from one ground rod to the other
without cutting or splicing and then
directly into the main circuit breaker
panel. If your main electrical panel
is in the basement, then you will need
to drill a hole slightly larger than
the wire (7/16" -5/8") into
your foundation wall or into your
siding near where it meets the
foundation.
Dig a
hole approximately one foot deep for
the insertion of each ground rod. The
holes should be one to two feet away
from the foundation to avoid contact
with the concrete footings of your
house. Then dig a
connecting trench close to the
foundation between the ground rod
holes. The trench is to facilitate the
connection of the unspliced continuous
grounding electrode conductor from ground rod to ground
rod and then to the main electrical
panel. Alternatively you can run a
wire from each ground rod directly to
your main electrical panel (As per
250.64(F)(2). You could also attach
the wire to the side of the house. The copper
wire should be no smaller than #6, but
I recommend at least a #4.
Take
one of the eight foot ground rods and
insert the pointy end into one of the
holes that you have dug. Stand on a
ladder and hammer it down into the
earth using a 3 pound or heavier
hammer in one hand while holding the
ground rod with the other. An
assistant would be good for holding
the rod as it tends to move around and
vibrate. It will probably go in easy
at first, but after a while it only
sinks in a very short distance with
each hammer blow. This would be a good
time to have a rotary hammer
with
a ground rod driver
attachment or a
jack hammer. After
you have one ground rod driven,
proceed to the next one.
Once
the ground rods are slightly below the
surface of the earth you can attach
the copper wire to them using the acorn style clamps . Depending on the
circumstances it may be easier to
start from the main electrical panel's
location and run the wire to the
ground rods from there. Run the wire
through the trench to the ground
rods and put it through the acorn
clamp with the wire between the clamp
and the rod. Do not put it
between the clamp screw and the
rod. I usually strip 4" - 6" of insulation off
and double the wire over to make good contact with the rod. Bring the
wire into the house through a small
hole in the foundation or siding and
continue on to the main electrical
panel. If you are running this in a
basement and need to cross some
joists, you should drill small holes
in the center of each joist and run
the wire through the joists instead of
under them. The wire should be secured
every 3' - 4' using cable staples if
you are running it on the side of a
joist. If you are using insulated
wire, it is a good idea to wrap green
electrical tape around it in a few
visible areas.
The
final connection is inside the main
electrical panel. Bring the grounding
electrode conductor
into the electrical panel through a
1/2" trade size (7/8"
actual) hole using a connector
approved for the grounding electrode
conductor. Sometimes the inspector
will accept clamp type metal
3/8" squeeze connector or a
plastic strain relief button. Each wire
must be terminated in it's own
termination screw terminal. If there
aren't any available screw terminals,
then you will need to add a terminal
bar in the main electrical panel.
After marking, drilling, and tapping
two holes (Usually 8/32 or 10/32),
screw the additional ground bar
directly to the metal enclosure of the
main electrical panel using fine
thread machine screws.
In the
2011 "National Electrical Code" article 250.94 requires an
"intersystem bonding termination". Basically a
means must be provided for other
utilities such as telephone and cable
TV to attach their own grounding
conductor. This must be located
near the electric meter. Several
manufacturers have products available
to easily meet this requirement by
merely attaching it to your grounding
electrode conductor and fastening it
to an outside wall or the electric meter.
When installing your grounding
electrode conductor leave a 8" -
12" loop in the area of the electric meter for this
terminal block to be installed later.
To
fully protect your home against
lightning it is imperative that the
cable TV service and the telephone
service be bonded to the grounding
electrode conductor. Use a #10 copper
wire to connect the cable TV at its
entrance point. There is usually a
screw terminal on the cable splitter
or termination point for grounding
purposes. The telephone demarcation
point or box should also have a
grounding terminal. Look for a green
screw or a lug. If you have a
satellite dish antenna it should also
be bonded to the "intersystem bonding termination"
as well as a regular TV
antenna.
Lastly
a bonding jumper must be installed
between your hot and cold water pipes
using water pipe ground clamps
and a
piece of #6 or #4 wire. This can
be done at any point along the piping
system, but is most commonly connected
at the water heater so that the
inspector can readily see it.
Bonding to the ground rods is
necessary to prevent lightning damage
to your home. Lightning wants to go to
earth, but sometimes things get in the
way and are sacrificed. By providing a good solid path to
earth via the grounding electrode
conductor and the ground rods you are
minimizing the damage that could
occur. The lightning strike does not
have be directly on your home. It
could hit a telephone pole across the
street and travel down the utility
wires until it finds a path to earth.
See the "Basics
of Surge Protection"
An
additional enhancement and level of protection can be made to your grounding electrode system by the installation of a
whole house surge protector.
This gets wired
directly into your electrical panel
and and is connected to a dedicated
two pole circuit
breaker.
Top
|