However
an "Intersystem Bonding
Termination" can be installed on
existing grounding electrode
conductors and are quite reasonable (A
few dollars) to purchase. They
can be found at an electrical supply
company and are made to attach to
existing wiring.
National
Electrical Code references:
Articles 250.50, 250.52, 250.53,
250.70, 250.94, 800.100(A), (B), (C)
& (D), 800.106, 820.100.
Other articles and codes may apply depending on
location, type of building and local
code requirements.
Usually
the "Intersystem Bonding
Termination" would get
attached to the grounding electrode
conductor that is attached to a ground rod near the outside electric
meter and the other utilities such as
telephone and cable & satellite
TV. An additional
"Intersystem Bonding
Termination" could also be installed indoors
near the electrical panel or near the
water pipe ground connection if
needed.
From
the "Intersystem Bonding
Termination" you would run
a solid #10 copper wire to the cable
TV terminal block or the satellite
dish. A #12 copper wire is
sufficient for the telephone
demarcation block.
Having
everything grounded and bonded
properly will help prevent damage or a
fire from lightning.